The reticulation controller has stopped working and requires investigation.

This is a high priority as it is very hot and the lawns and gardens will die quickly without water.

Author:  TheMews [ Sat Dec 23, 2017 6:24 am ]
Post subject:  Re: Reticulation controller fault

After investigation we have determined there was an electrical fault in the "contactor" that controls the bore pump.

Unfortunately this fault has caused an upstream fault in the reticulation controller which now requires replacement.

We have ordered a new controller and arranged an electrician to attend next week to inspect the contactor and advise what repairs need to be made.

Attachments:
20171222_170012.jpg
20171222_170012.jpg [ 299.35 KiB | Viewed 7134 times ]

Author:  TheMews [ Thu Dec 28, 2017 11:48 am ]
Post subject:  Re: Reticulation controller fault

The faulty contactor has been replaced and is now working as expected

A temporary solution has been put in place to allow watering until the new controller arrives.

Author:  TheMews [ Sun Jan 07, 2018 10:20 am ]
Post subject:  Re: Reticulation controller fault

The new reticulation controller has been installed, programmed and tested.

This maintenance item is now completed